Appliance 250 nominal power and airflow?
Hi all,
Does anyone know the answers to the following technical specs of the RSA SecurID Hardware Appliance 250?
- Nominal Power
- Airflow: Is it a front-to-back cooling?
I've searched through the 'EMC® SVR-I1U-1208 Server Installation and Maintenance Guide', downloaded from here: https://community.rsa.com/docs/DOC-45077 , but I don't think it's stated there (unless i've mistakenly missed it).
Many thanks!
Regards,
Adibah
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
For the Intel 250
Yes, front to back.
Six dual rotor managed system fans
One power supply fan for each installed power supply module
Power supply: Two 750W Platinum (1+1) Redundant Hot-swap Capable
Power Supply Specification:
Wattage | 750W (Energy Smart) |
Voltage | 90 – 264 VAC, auto-ranging, 47 Hz-63 Hz |
Heat Dissipation | 2560 BTU/hr |
Maximum Inrush Current | Under typical line conditions and over the entire system ambient operating range, the inrush current may reach 55 A per power supply for up to 5ms |
80 Plus rating | Platinum |
Climate Saver (CS) rating | Platinum |
|
Temperature | |
Operating | 10° to 35°C (50° to 95°F) with a maximum rate of change not to exceed 10°C per hour |
Non-Operating | -40° to 65°C (-40° to 149°F) |
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
For the Intel 250
Yes, front to back.
Six dual rotor managed system fans
One power supply fan for each installed power supply module
Power supply: Two 750W Platinum (1+1) Redundant Hot-swap Capable
Power Supply Specification:
Wattage | 750W (Energy Smart) |
Voltage | 90 – 264 VAC, auto-ranging, 47 Hz-63 Hz |
Heat Dissipation | 2560 BTU/hr |
Maximum Inrush Current | Under typical line conditions and over the entire system ambient operating range, the inrush current may reach 55 A per power supply for up to 5ms |
80 Plus rating | Platinum |
Climate Saver (CS) rating | Platinum |
|
Temperature | |
Operating | 10° to 35°C (50° to 95°F) with a maximum rate of change not to exceed 10°C per hour |
Non-Operating | -40° to 65°C (-40° to 149°F) |